Never push the Big Red Button (New York City subway failure)
NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
OUTAGE ISSUE ON AUGUST 29, 2021
Key Findings
September 8, 2021


https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf

Key Findings
[...]

3. Based on the electrical equipment log readings and the manufacturer’s
official assessment, it was determined that the most likely cause of RCC
shutdown was the “Emergency Power Off” button being manually activated.

Secondary Findings

1. The “Emergency Power Off” button did not have a protective cover at the
time of the shutdown or the following WSP investigation.

[...]
Mitigation Steps

1. Set up the electrical equipment Control and Communication systems
properly to stay active so that personnel can monitor RCC electrical
system operations.

[...]
RE: Never push the Big Red Button (New York City subway failure) [ In reply to ]
Reminds me of something that happened about 25 years ago when an elementary school visited our data center of the insurance company where I worked. One of our operators strategically positioned himself between the kids and the mainframe, leaned back and hit it's EPO button.

Matthew Huff | Director of Technical Operations | OTA Management LLC

Office: 914-460-4039
mhuff@ox.com | www.ox.com
...........................................................................................................................................

-----Original Message-----
From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org> On Behalf Of Sean Donelan
Sent: Friday, September 10, 2021 12:38 PM
To: nanog@nanog.org
Subject: Never push the Big Red Button (New York City subway failure)

NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
OUTAGE ISSUE ON AUGUST 29, 2021
Key Findings
September 8, 2021


https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf

Key Findings
[...]

3. Based on the electrical equipment log readings and the manufacturer’s
official assessment, it was determined that the most likely cause of RCC
shutdown was the “Emergency Power Off” button being manually activated.

Secondary Findings

1. The “Emergency Power Off” button did not have a protective cover at the
time of the shutdown or the following WSP investigation.

[...]
Mitigation Steps

1. Set up the electrical equipment Control and Communication systems
properly to stay active so that personnel can monitor RCC electrical
system operations.

[...]
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff <mhuff@ox.com> wrote:

> Reminds me of something that happened about 25 years ago when an
> elementary school visited our data center of the insurance company where I
> worked. One of our operators strategically positioned himself between the
> kids and the mainframe, leaned back and hit it's EPO button.
>
>
Or when your building engineering team cuts themselves a new key for the
'main breaker' for the facility... and tests it at 2pm on a tuesday.
Or when that same team cuts a second key (gotta have 2 keys!) and tests
that key on the same 'main breaker' ... at 2pm on the following tuesday.

<quadruple face palm>

not fakenews, a real story from a large building full of gov't employees
and computers and all manner of 'critical infrastructure' for the agency
occupying said building.

Matthew Huff | Director of Technical Operations | OTA Management LLC
>
> Office: 914-460-4039
> mhuff@ox.com | www.ox.com
>
> ...........................................................................................................................................
>
> -----Original Message-----
> From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org> On Behalf Of Sean
> Donelan
> Sent: Friday, September 10, 2021 12:38 PM
> To: nanog@nanog.org
> Subject: Never push the Big Red Button (New York City subway failure)
>
> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
> OUTAGE ISSUE ON AUGUST 29, 2021
> Key Findings
> September 8, 2021
>
>
>
> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>
> Key Findings
> [...]
>
> 3. Based on the electrical equipment log readings and the manufacturer’s
> official assessment, it was determined that the most likely cause of RCC
> shutdown was the “Emergency Power Off” button being manually activated.
>
> Secondary Findings
>
> 1. The “Emergency Power Off” button did not have a protective cover at the
> time of the shutdown or the following WSP investigation.
>
> [...]
> Mitigation Steps
>
> 1. Set up the electrical equipment Control and Communication systems
> properly to stay active so that personnel can monitor RCC electrical
> system operations.
>
> [...]
>
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
True EPO story; maintenance crew carrying new drywall into the data center
backed into the EPO that didn't have a cover on it. One of the most
eerie sounds in networking...a completely silent data center.

-chris

On Fri, Sep 10, 2021 at 2:48 PM Christopher Morrow <morrowc.lists@gmail.com>
wrote:

>
>
> On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff <mhuff@ox.com> wrote:
>
>> Reminds me of something that happened about 25 years ago when an
>> elementary school visited our data center of the insurance company where I
>> worked. One of our operators strategically positioned himself between the
>> kids and the mainframe, leaned back and hit it's EPO button.
>>
>>
> Or when your building engineering team cuts themselves a new key for the
> 'main breaker' for the facility... and tests it at 2pm on a tuesday.
> Or when that same team cuts a second key (gotta have 2 keys!) and tests
> that key on the same 'main breaker' ... at 2pm on the following tuesday.
>
> <quadruple face palm>
>
> not fakenews, a real story from a large building full of gov't employees
> and computers and all manner of 'critical infrastructure' for the agency
> occupying said building.
>
> Matthew Huff | Director of Technical Operations | OTA Management LLC
>>
>> Office: 914-460-4039
>> mhuff@ox.com | www.ox.com
>>
>> ...........................................................................................................................................
>>
>> -----Original Message-----
>> From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org> On Behalf Of Sean
>> Donelan
>> Sent: Friday, September 10, 2021 12:38 PM
>> To: nanog@nanog.org
>> Subject: Never push the Big Red Button (New York City subway failure)
>>
>> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
>> OUTAGE ISSUE ON AUGUST 29, 2021
>> Key Findings
>> September 8, 2021
>>
>>
>>
>> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>>
>> Key Findings
>> [...]
>>
>> 3. Based on the electrical equipment log readings and the manufacturer’s
>> official assessment, it was determined that the most likely cause of RCC
>> shutdown was the “Emergency Power Off” button being manually activated.
>>
>> Secondary Findings
>>
>> 1. The “Emergency Power Off” button did not have a protective cover at
>> the
>> time of the shutdown or the following WSP investigation.
>>
>> [...]
>> Mitigation Steps
>>
>> 1. Set up the electrical equipment Control and Communication systems
>> properly to stay active so that personnel can monitor RCC electrical
>> system operations.
>>
>> [...]
>>
>

--
Chris Kane
RE: Never push the Big Red Button (New York City subway failure) [ In reply to ]
Since we are telling power horror stories…


How about the call from the night operator that arrived at 10:00pm asking “Is there any reason there is no power in the data center?”

Turns out someone had plugged in a new high end workgroup laser printer to the outside wall of the datacenter. The power receptacle was wired into the data center’s UPS and completely smoked the UPS. Luckily the static transfer switched worked, but the three mainframes weren’t’ happy…


Or

Our building had a major ground fault issue that took years to find and resolve. We got hit with lightning that caused the mainframe to fault and recycle…and two minutes in, we got hit by lightning again. When the system failed to start, we called IBM support. When we explained what happened there was a very long pause…then some mumbling off phone, then the manager got on the line and said someone would be flying out and be onsite within 12 hours. We were down for 3 days, and got fined $250,000 by the insurance regulators since we couldn’t pay claims.

Matthew Huff | Director of Technical Operations | OTA Management LLC

Office: 914-460-4039
mhuff@ox.com<mailto:mhuff@ox.com> | www.ox.com<http://www.ox.com>
...........................................................................................................................................

From: Chris Kane <ccie14430@gmail.com>
Sent: Friday, September 10, 2021 3:16 PM
To: Christopher Morrow <morrowc.lists@gmail.com>
Cc: Matthew Huff <mhuff@ox.com>; nanog@nanog.org
Subject: Re: Never push the Big Red Button (New York City subway failure)

True EPO story; maintenance crew carrying new drywall into the data center backed into the EPO that didn't have a cover on it. One of the most eerie sounds in networking...a completely silent data center.

-chris

On Fri, Sep 10, 2021 at 2:48 PM Christopher Morrow <morrowc.lists@gmail.com<mailto:morrowc.lists@gmail.com>> wrote:


On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff <mhuff@ox.com<mailto:mhuff@ox.com>> wrote:
Reminds me of something that happened about 25 years ago when an elementary school visited our data center of the insurance company where I worked. One of our operators strategically positioned himself between the kids and the mainframe, leaned back and hit it's EPO button.

Or when your building engineering team cuts themselves a new key for the 'main breaker' for the facility... and tests it at 2pm on a tuesday.
Or when that same team cuts a second key (gotta have 2 keys!) and tests that key on the same 'main breaker' ... at 2pm on the following tuesday.

<quadruple face palm>

not fakenews, a real story from a large building full of gov't employees and computers and all manner of 'critical infrastructure' for the agency occupying said building.

Matthew Huff | Director of Technical Operations | OTA Management LLC

Office: 914-460-4039
mhuff@ox.com<mailto:mhuff@ox.com> | www.ox.com<http://www.ox.com>
...........................................................................................................................................

-----Original Message-----
From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org<mailto:ox.com@nanog.org>> On Behalf Of Sean Donelan
Sent: Friday, September 10, 2021 12:38 PM
To: nanog@nanog.org<mailto:nanog@nanog.org>
Subject: Never push the Big Red Button (New York City subway failure)

NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
OUTAGE ISSUE ON AUGUST 29, 2021
Key Findings
September 8, 2021


https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf

Key Findings
[...]

3. Based on the electrical equipment log readings and the manufacturer’s
official assessment, it was determined that the most likely cause of RCC
shutdown was the “Emergency Power Off” button being manually activated.

Secondary Findings

1. The “Emergency Power Off” button did not have a protective cover at the
time of the shutdown or the following WSP investigation.

[...]
Mitigation Steps

1. Set up the electrical equipment Control and Communication systems
properly to stay active so that personnel can monitor RCC electrical
system operations.

[...]


--
Chris Kane
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Fri, 10 Sep 2021, Sean Donelan wrote:

> 1. The “Emergency Power Off” button did not have a protective cover at the
> time of the shutdown or the following WSP investigation.

Aka "molly-guard".

https://en.wiktionary.org/wiki/molly-guard

--
Mikael Abrahamsson email: swmike@swm.pp.se
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Fri, Sep 10, 2021 at 2:52 PM Christopher Morrow <morrowc.lists@gmail.com>
wrote:

>
>
> On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff <mhuff@ox.com> wrote:
>
>> Reminds me of something that happened about 25 years ago when an
>> elementary school visited our data center of the insurance company where I
>> worked. One of our operators strategically positioned himself between the
>> kids and the mainframe, leaned back and hit it's EPO button.
>>
>>
> Or when your building engineering team cuts themselves a new key for the
> 'main breaker' for the facility... and tests it at 2pm on a tuesday.
> Or when that same team cuts a second key (gotta have 2 keys!) and tests
> that key on the same 'main breaker' ... at 2pm on the following tuesday.
>
> <quadruple face palm>
>
> not fakenews, a real story from a large building full of gov't employees
> and computers and all manner of 'critical infrastructure' for the agency
> occupying said building.
>


In the early 2000s a friend of mine worked for a company in NYC
that provided stock feeds to large banks and brokerages and similar. They'd
ship a (locked) cabinet full of stuff to their customers, complete with an
Ethernet cable stickin' out the back. Customer would plug this into their
network and, um, do whatever it is stock people do. There was some
horrendously expensive SLA attached, and so they outsourced support to one
of the managed services companies so that they could provide 24x7x2hour
response all over the country.


One day, one of their largest customers, a large bank, also in NYC is down.
This means that the brokerage arm is unable to do any trades, and so is,
um, annoyed. Support rushes over to the customer and "fix it". My friend
doesn't really get a good explanation of how it got fixed, but, meh, it's
working, so all good. A few weeks later, same thing - customer devices
disappear from monitoring, smart-hands/support rush over and fix it, no
useful RFO. This happens a few more times, and everyone is getting
increasingly annoyed.

Eventually my friend arranges it so that he gets paged at the same time as
the support provider. Pager goes off, friend jumps in a cab to the
customer. He arrives at the same time as the smart-hands person, who,
oddly, is clutching 1: an Ethernet face-plate and 2: a punch-down tool.
Somewhat mystified, my friend follows the support person to where the
cabinet is located. Because it's important and special, but not actually
bank owned, it cannot live in their data-center... and so it is located in
the corridor, just outside the server room.

Because of where the Ethernet cable comes out the back of the cabinet, and
where the wall jack is, there is basically no slack. When someone goes in
or out, especially if they are wheeling a cart or carrying a box of
equipment, they bang into the cabinet, which slowly rolls away -- ripping
the wall jack off the wall, and the cable out the back of the jack.
Support's "solution" to this has been to punch down the cable onto a new
wall jack, screw it back onto the wall, wheel the cabinet back into place,
and call it fixed.

My friend screwed down the cabinet feet, so it wasn't resting on the wheels
any more, replaced the 6ft Ethernet with a 15ft, and the issue never
recurred :-P

W




>
> Matthew Huff | Director of Technical Operations | OTA Management LLC
>>
>> Office: 914-460-4039
>> mhuff@ox.com | www.ox.com
>>
>> ...........................................................................................................................................
>>
>> -----Original Message-----
>> From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org> On Behalf Of Sean
>> Donelan
>> Sent: Friday, September 10, 2021 12:38 PM
>> To: nanog@nanog.org
>> Subject: Never push the Big Red Button (New York City subway failure)
>>
>> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
>> OUTAGE ISSUE ON AUGUST 29, 2021
>> Key Findings
>> September 8, 2021
>>
>>
>>
>> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>>
>> Key Findings
>> [...]
>>
>> 3. Based on the electrical equipment log readings and the manufacturer’s
>> official assessment, it was determined that the most likely cause of RCC
>> shutdown was the “Emergency Power Off” button being manually activated.
>>
>> Secondary Findings
>>
>> 1. The “Emergency Power Off” button did not have a protective cover at
>> the
>> time of the shutdown or the following WSP investigation.
>>
>> [...]
>> Mitigation Steps
>>
>> 1. Set up the electrical equipment Control and Communication systems
>> properly to stay active so that personnel can monitor RCC electrical
>> system operations.
>>
>> [...]
>>
>

--
The computing scientist’s main challenge is not to get confused by the
complexities of his own making.
-- E. W. Dijkstra
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
A nearby datacenter once lost power delayed because someone hit the switch
to transfer from city power to generator power and then failed to notice.
The power went out the day after when there was no fuel left.

On Fri, Sep 10, 2021 at 9:24 PM Matthew Huff <mhuff@ox.com> wrote:

> Since we are telling power horror stories…
>
>
>
>
>
> How about the call from the night operator that arrived at 10:00pm asking
> “Is there any reason there is no power in the data center?”
>
>
>
> Turns out someone had plugged in a new high end workgroup laser printer to
> the outside wall of the datacenter. The power receptacle was wired into the
> data center’s UPS and completely smoked the UPS. Luckily the static
> transfer switched worked, but the three mainframes weren’t’ happy…
>
>
>
>
>
> Or
>
>
>
> Our building had a major ground fault issue that took years to find and
> resolve. We got hit with lightning that caused the mainframe to fault and
> recycle…and two minutes in, we got hit by lightning again. When the system
> failed to start, we called IBM support. When we explained what happened
> there was a very long pause…then some mumbling off phone, then the manager
> got on the line and said someone would be flying out and be onsite within
> 12 hours. We were down for 3 days, and got fined $250,000 by the insurance
> regulators since we couldn’t pay claims.
>
>
>
> *Matthew Huff* | Director of Technical Operations | OTA Management LLC
>
>
>
> *Office: 914-460-4039*
>
> *mhuff@ox.com <mhuff@ox.com> | **www.ox.com <http://www.ox.com>*
>
>
> *...........................................................................................................................................*
>
>
>
> *From:* Chris Kane <ccie14430@gmail.com>
> *Sent:* Friday, September 10, 2021 3:16 PM
> *To:* Christopher Morrow <morrowc.lists@gmail.com>
> *Cc:* Matthew Huff <mhuff@ox.com>; nanog@nanog.org
> *Subject:* Re: Never push the Big Red Button (New York City subway
> failure)
>
>
>
> True EPO story; maintenance crew carrying new drywall into the data center
> backed into the EPO that didn't have a cover on it. One of the most
> eerie sounds in networking...a completely silent data center.
>
>
>
> -chris
>
>
>
> On Fri, Sep 10, 2021 at 2:48 PM Christopher Morrow <
> morrowc.lists@gmail.com> wrote:
>
>
>
>
>
> On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff <mhuff@ox.com> wrote:
>
> Reminds me of something that happened about 25 years ago when an
> elementary school visited our data center of the insurance company where I
> worked. One of our operators strategically positioned himself between the
> kids and the mainframe, leaned back and hit it's EPO button.
>
>
>
> Or when your building engineering team cuts themselves a new key for the
> 'main breaker' for the facility... and tests it at 2pm on a tuesday.
>
> Or when that same team cuts a second key (gotta have 2 keys!) and tests
> that key on the same 'main breaker' ... at 2pm on the following tuesday.
>
>
>
> <quadruple face palm>
>
>
>
> not fakenews, a real story from a large building full of gov't employees
> and computers and all manner of 'critical infrastructure' for the agency
> occupying said building.
>
>
>
> Matthew Huff | Director of Technical Operations | OTA Management LLC
>
> Office: 914-460-4039
> mhuff@ox.com | www.ox.com
>
> ...........................................................................................................................................
>
> -----Original Message-----
> From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org> On Behalf Of Sean
> Donelan
> Sent: Friday, September 10, 2021 12:38 PM
> To: nanog@nanog.org
> Subject: Never push the Big Red Button (New York City subway failure)
>
> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
> OUTAGE ISSUE ON AUGUST 29, 2021
> Key Findings
> September 8, 2021
>
>
>
> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>
> Key Findings
> [...]
>
> 3. Based on the electrical equipment log readings and the manufacturer’s
> official assessment, it was determined that the most likely cause of RCC
> shutdown was the “Emergency Power Off” button being manually activated.
>
> Secondary Findings
>
> 1. The “Emergency Power Off” button did not have a protective cover at the
> time of the shutdown or the following WSP investigation.
>
> [...]
> Mitigation Steps
>
> 1. Set up the electrical equipment Control and Communication systems
> properly to stay active so that personnel can monitor RCC electrical
> system operations.
>
> [...]
>
>
>
>
> --
>
> Chris Kane
>
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Fri, Sep 10, 2021 at 4:21 PM Baldur Norddahl <baldur.norddahl@gmail.com>
wrote:

> A nearby datacenter once lost power delayed because someone hit the switch
> to transfer from city power to generator power and then failed to notice.
> The power went out the day after when there was no fuel left.
>

:-)

A story, told to me by a friend...

The utility let them know that they were going to be doing some
maintenance work in the area. No impact expected, but out of an abundance
of caution, they transfer over to generators. After the utility lets them
know that the maintenance work is all finished, they want to switch back.
If the generators are "emergency power", and you need to switch back to
"utility power", obviously the way to do this must be the big red button,
clearly marked as "EMERGENCY POWER OFF", no?!

I suspect it is apocryphal, but it's still entertaining,
W



>
> On Fri, Sep 10, 2021 at 9:24 PM Matthew Huff <mhuff@ox.com> wrote:
>
>> Since we are telling power horror stories…
>>
>>
>>
>>
>>
>> How about the call from the night operator that arrived at 10:00pm asking
>> “Is there any reason there is no power in the data center?”
>>
>>
>>
>> Turns out someone had plugged in a new high end workgroup laser printer
>> to the outside wall of the datacenter. The power receptacle was wired into
>> the data center’s UPS and completely smoked the UPS. Luckily the static
>> transfer switched worked, but the three mainframes weren’t’ happy…
>>
>>
>>
>>
>>
>> Or
>>
>>
>>
>> Our building had a major ground fault issue that took years to find and
>> resolve. We got hit with lightning that caused the mainframe to fault and
>> recycle…and two minutes in, we got hit by lightning again. When the system
>> failed to start, we called IBM support. When we explained what happened
>> there was a very long pause…then some mumbling off phone, then the manager
>> got on the line and said someone would be flying out and be onsite within
>> 12 hours. We were down for 3 days, and got fined $250,000 by the insurance
>> regulators since we couldn’t pay claims.
>>
>>
>>
>> *Matthew Huff* | Director of Technical Operations | OTA Management LLC
>>
>>
>>
>> *Office: 914-460-4039*
>>
>> *mhuff@ox.com <mhuff@ox.com> | **www.ox.com <http://www.ox.com>*
>>
>>
>> *...........................................................................................................................................*
>>
>>
>>
>> *From:* Chris Kane <ccie14430@gmail.com>
>> *Sent:* Friday, September 10, 2021 3:16 PM
>> *To:* Christopher Morrow <morrowc.lists@gmail.com>
>> *Cc:* Matthew Huff <mhuff@ox.com>; nanog@nanog.org
>> *Subject:* Re: Never push the Big Red Button (New York City subway
>> failure)
>>
>>
>>
>> True EPO story; maintenance crew carrying new drywall into the data
>> center backed into the EPO that didn't have a cover on it. One of the most
>> eerie sounds in networking...a completely silent data center.
>>
>>
>>
>> -chris
>>
>>
>>
>> On Fri, Sep 10, 2021 at 2:48 PM Christopher Morrow <
>> morrowc.lists@gmail.com> wrote:
>>
>>
>>
>>
>>
>> On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff <mhuff@ox.com> wrote:
>>
>> Reminds me of something that happened about 25 years ago when an
>> elementary school visited our data center of the insurance company where I
>> worked. One of our operators strategically positioned himself between the
>> kids and the mainframe, leaned back and hit it's EPO button.
>>
>>
>>
>> Or when your building engineering team cuts themselves a new key for the
>> 'main breaker' for the facility... and tests it at 2pm on a tuesday.
>>
>> Or when that same team cuts a second key (gotta have 2 keys!) and tests
>> that key on the same 'main breaker' ... at 2pm on the following tuesday.
>>
>>
>>
>> <quadruple face palm>
>>
>>
>>
>> not fakenews, a real story from a large building full of gov't employees
>> and computers and all manner of 'critical infrastructure' for the agency
>> occupying said building.
>>
>>
>>
>> Matthew Huff | Director of Technical Operations | OTA Management LLC
>>
>> Office: 914-460-4039
>> mhuff@ox.com | www.ox.com
>>
>> ...........................................................................................................................................
>>
>> -----Original Message-----
>> From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org> On Behalf Of Sean
>> Donelan
>> Sent: Friday, September 10, 2021 12:38 PM
>> To: nanog@nanog.org
>> Subject: Never push the Big Red Button (New York City subway failure)
>>
>> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
>> OUTAGE ISSUE ON AUGUST 29, 2021
>> Key Findings
>> September 8, 2021
>>
>>
>>
>> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>>
>> Key Findings
>> [...]
>>
>> 3. Based on the electrical equipment log readings and the manufacturer’s
>> official assessment, it was determined that the most likely cause of RCC
>> shutdown was the “Emergency Power Off” button being manually activated.
>>
>> Secondary Findings
>>
>> 1. The “Emergency Power Off” button did not have a protective cover at
>> the
>> time of the shutdown or the following WSP investigation.
>>
>> [...]
>> Mitigation Steps
>>
>> 1. Set up the electrical equipment Control and Communication systems
>> properly to stay active so that personnel can monitor RCC electrical
>> system operations.
>>
>> [...]
>>
>>
>>
>>
>> --
>>
>> Chris Kane
>>
>

--
The computing scientist’s main challenge is not to get confused by the
complexities of his own making.
-- E. W. Dijkstra
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
----- Original Message -----
> From: "Sean Donelan" <sean@donelan.com>

> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
> OUTAGE ISSUE ON AUGUST 29, 2021
> Key Findings
> September 8, 2021
>
> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>
> Key Findings
> [...]
>
> 3. Based on the electrical equipment log readings and the manufacturer’s
> official assessment, it was determined that the most likely cause of RCC
> shutdown was the “Emergency Power Off” button being manually activated.

I don't even *do* datacenter for a living, and I know that when you hit the
Molly button,

1) A Klaxon goes off in the Data Center -- one that sounds *different* from
the Halon Klaxon, in both cadence and tone (just for a couple bursts), and

2) Yellow rotating beacons turn on, and stay on while you're on Emergency Power.

Yes, real honest-to-ghod *rotating mechanical beacons*, none of this flashing LED
crap.

Clearly, it's important that the use of Emergency Power be annoyingly noticeable.

Cheers,
-- jra
--
Jay R. Ashworth Baylink jra@baylink.com
Designer The Things I Think RFC 2100
Ashworth & Associates http://www.bcp38.info 2000 Land Rover DII
St Petersburg FL USA BCP38: Ask For It By Name! +1 727 647 1274
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
Now I'm curious... in all of the DCs and COs I've worked in - to the best of my knowledge, I haven't personally tested this! - the EPO button does not? switch to emergency power. It turns off ALL equipment power in the space - no lights, no klaxons, nothing. In simpler setups, the EPO is connected to the UPS so anything plugged in to the UPS does dark instantly. In one DC I'm familiar with, the EPO switch kills all the UPS output and? uses several relays to kill commercial power at the same time.
In some, the room lights were not covered by the EPO switch, in some they were. Emergency exit lamps will continue to be lit, as they have internal batteries, and are required by building/fire code.

Is it (somewhat) common for an EPO switch to only disconnect commercial power and leave local redundant power live? What sort of facilities would have this?

-Adam

Adam Thompson
Consultant, Infrastructure Services
[1593169877849]
100 - 135 Innovation Drive
Winnipeg, MB, R3T 6A8
(204) 977-6824 or 1-800-430-6404 (MB only)
athompson@merlin.mb.ca<mailto:athompson@merlin.mb.ca>
www.merlin.mb.ca<http://www.merlin.mb.ca/>
________________________________
From: NANOG <nanog-bounces+athompson=merlin.mb.ca@nanog.org> on behalf of Jay R. Ashworth <jra@baylink.com>
Sent: September 11, 2021 22:23
To: nanog <nanog@nanog.org>
Subject: Re: Never push the Big Red Button (New York City subway failure)

----- Original Message -----
> From: "Sean Donelan" <sean@donelan.com>

> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
> OUTAGE ISSUE ON AUGUST 29, 2021
> Key Findings
> September 8, 2021
>
> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>
> Key Findings
> [...]
>
> 3. Based on the electrical equipment log readings and the manufacturer’s
> official assessment, it was determined that the most likely cause of RCC
> shutdown was the “Emergency Power Off” button being manually activated.

I don't even *do* datacenter for a living, and I know that when you hit the
Molly button,

1) A Klaxon goes off in the Data Center -- one that sounds *different* from
the Halon Klaxon, in both cadence and tone (just for a couple bursts), and

2) Yellow rotating beacons turn on, and stay on while you're on Emergency Power.

Yes, real honest-to-ghod *rotating mechanical beacons*, none of this flashing LED
crap.

Clearly, it's important that the use of Emergency Power be annoyingly noticeable.

Cheers,
-- jra
--
Jay R. Ashworth Baylink jra@baylink.com
Designer The Things I Think RFC 2100
Ashworth & Associates http://www.bcp38.info 2000 Land Rover DII
St Petersburg FL USA BCP38: Ask For It By Name! +1 727 647 1274
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
> On Sep 15, 2021, at 10:58 AM, Adam Thompson <athompson@merlin.mb.ca> wrote:
>
> Now I'm curious... in all of the DCs and COs I've worked in - to the best of my knowledge, I haven't personally tested this! - the EPO button does not? switch to emergency power. It turns off ALL equipment power in the space - no lights, no klaxons, nothing. In simpler setups, the EPO is connected to the UPS so anything plugged in to the UPS does dark instantly. In one DC I'm familiar with, the EPO switch kills all the UPS output and? uses several relays to kill commercial power at the same time.
> In some, the room lights were not covered by the EPO switch, in some they were. Emergency exit lamps will continue to be lit, as they have internal batteries, and are required by building/fire code.

It was always my understanding EPO was to be used for “We have an electrical fire and need to remove the source RFN”, not “we need to be on the redundant power instead of city power and don’t want to wait for the automatic transfer”.
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On 9/15/21 08:58, Adam Thompson wrote:
> Now I'm curious... in all of the DCs and COs I've worked in - to the
> best of my knowledge, I haven't personally tested this! - the EPO button
> does *not*? switch to emergency power.  It turns off ALL equipment power
> in the space - no lights, no klaxons, nothing.  In simpler setups, the
> EPO is connected to the UPS so anything plugged in to the UPS does dark
> instantly.  In one DC I'm familiar with, the EPO switch kills all the
> UPS output *and*? uses several relays to kill commercial power at the
> same time.

That's my understanding as well. Not necessarily the room lights
depending on the facility, but all equipment power. To be used if the
space is on fire or someone is in the process of being electrocuted.

I've never seen a klaxon or audible alarm connected with EPO. Things
just get very quiet.

--
Jay Hennigan - jay@west.net
Network Engineering - CCIE #7880
503 897-8550 - WB6RDV
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Wed, Sep 15, 2021 at 9:21 AM Daniel Seagraves
<dseagrav@humancapitaldev.com> wrote:
> It was always my understanding EPO was to be used for
> “We have an electrical fire and need to remove the source RFN”,
> not “we need to be on the redundant power instead of city power
> and don’t want to wait for the automatic transfer”.

Hi Daniel,

That's correct. I'm not sure what Jay was on about, but the EPO button
kills power to everything that would otherwise be protected from a
building power failure. There's generally no warning; you know it
happened from the rapid silence.

I've also never seen warning lights that the facility is on emergency
power. It's probably a good idea but I've never seen it.

Regards,
Bill Herrin

--
William Herrin
bill@herrin.us
https://bill.herrin.us/
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Wed, Sep 15, 2021 at 12:23 PM Daniel Seagraves <
dseagrav@humancapitaldev.com> wrote:

>
> On Sep 15, 2021, at 10:58 AM, Adam Thompson <athompson@merlin.mb.ca>
> wrote:
>
> Now I'm curious... in all of the DCs and COs I've worked in - to the best
> of my knowledge, I haven't personally tested this! - the EPO button does
> *not* switch to emergency power. It turns off ALL equipment power in the
> space - no lights, no klaxons, nothing. In simpler setups, the EPO is
> connected to the UPS so anything plugged in to the UPS does dark
> instantly. In one DC I'm familiar with, the EPO switch kills all the UPS
> output *and* uses several relays to kill commercial power at the same
> time.
> In some, the room lights were not covered by the EPO switch, in some they
> were. Emergency exit lamps will continue to be lit, as they have internal
> batteries, and are required by building/fire code.
>
>
> It was always my understanding EPO was to be used for “We have an
> electrical fire and need to remove the source RFN”, not “we need to be on
> the redundant power instead of city power and don’t want to wait for the
> automatic transfer”.
>
>
Well, there is the EPO button, which generally does that, and the
(variously labeled) HALON/FM-200/GAS FIRE SUPPRESSION/GAS DISCHARGE button,
which does the flashy lights and klangly bell and similar. This is fairly
much always required by code, to give people time to evacuate before the
gas dumps and they suffocate. People often refer to both of these as EPOs
(or "the buttons that must not be pressed unless you have a REALLY good
reason.").

When I grew up (in South Africa), Halon/BCF was still in active use. When
there was a fire (or you pressed and held the big red HALON button) a siren
would sound and lights would flash for a few seconds to allow everyone time
to evacuate the machine room.
I'm assuming that things are now less stupid, but at the local University,
the BCF was stored in large gas bottles, with a pyrotechnic valve to
release it. The pyrotechnic charge was initiated with LA/LS (Lead
Azide/Lead Styphnate) hot-wire initiators, which were supposed to be
replaced every 2 years as part of some maintenance schedule - when LA/LS
ages, especially in the presence of humidity, it apparently can form a much
more sensitive crystal structure, which is very shock sensitive.

The system was installed in the 1960s, and the initiators were replaced
once or twice. Eventually, however, with sanctions, especially on things
that can be made to go boom, it became hard to get replacements, and so
they stopped replacing them... and eventually forgot about them ......
right up until sometime in the early 1990s, when someone accidentally
knocked into the bottles with a loaded equipment cart.
By this time the initiators had become sufficiently old and ornery that
they decided that they'd had enough, and set off the pyro charges, which
dumped all of the Halon into the room.

Luckily everyone survived, but IIRC, two people passed out before making it
to the door, and someone had to rush in and pull them to fresh air. The
added gas pressure also cracked the big glass window (what's the point in
having a big mainframe with flashy lights and spinning tapes if you cannot
show it off?), and also caused a few head-crashes.

W


--
The computing scientist’s main challenge is not to get confused by the
complexities of his own making.
-- E. W. Dijkstra
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
>
> If the generators are "emergency power", and you need to switch back to
> "utility power", obviously the way to do this must be the big red button,
> clearly marked as "EMERGENCY POWER OFF", no?!
>

The owner of my previous company did the same thing to us many years ago
because there was a small smudge on the placard between POWER and OFF that
he interpreted as a dash.

He was never happy with the custom sign I hung after that, REVENUE
REDUCTION SWITCH. But he never tried to be helpful after that, so
mission accomplished.

On Fri, Sep 10, 2021 at 4:35 PM Warren Kumari <warren@kumari.net> wrote:

>
>
> On Fri, Sep 10, 2021 at 4:21 PM Baldur Norddahl <baldur.norddahl@gmail.com>
> wrote:
>
>> A nearby datacenter once lost power delayed because someone hit the
>> switch to transfer from city power to generator power and then failed to
>> notice. The power went out the day after when there was no fuel left.
>>
>
> :-)
>
> A story, told to me by a friend...
>
> The utility let them know that they were going to be doing some
> maintenance work in the area. No impact expected, but out of an abundance
> of caution, they transfer over to generators. After the utility lets them
> know that the maintenance work is all finished, they want to switch back.
> If the generators are "emergency power", and you need to switch back to
> "utility power", obviously the way to do this must be the big red button,
> clearly marked as "EMERGENCY POWER OFF", no?!
>
> I suspect it is apocryphal, but it's still entertaining,
> W
>
>
>
>>
>> On Fri, Sep 10, 2021 at 9:24 PM Matthew Huff <mhuff@ox.com> wrote:
>>
>>> Since we are telling power horror stories…
>>>
>>>
>>>
>>>
>>>
>>> How about the call from the night operator that arrived at 10:00pm
>>> asking “Is there any reason there is no power in the data center?”
>>>
>>>
>>>
>>> Turns out someone had plugged in a new high end workgroup laser printer
>>> to the outside wall of the datacenter. The power receptacle was wired into
>>> the data center’s UPS and completely smoked the UPS. Luckily the static
>>> transfer switched worked, but the three mainframes weren’t’ happy…
>>>
>>>
>>>
>>>
>>>
>>> Or
>>>
>>>
>>>
>>> Our building had a major ground fault issue that took years to find and
>>> resolve. We got hit with lightning that caused the mainframe to fault and
>>> recycle…and two minutes in, we got hit by lightning again. When the system
>>> failed to start, we called IBM support. When we explained what happened
>>> there was a very long pause…then some mumbling off phone, then the manager
>>> got on the line and said someone would be flying out and be onsite within
>>> 12 hours. We were down for 3 days, and got fined $250,000 by the insurance
>>> regulators since we couldn’t pay claims.
>>>
>>>
>>>
>>> *Matthew Huff* | Director of Technical Operations | OTA Management LLC
>>>
>>>
>>>
>>> *Office: 914-460-4039*
>>>
>>> *mhuff@ox.com <mhuff@ox.com> | **www.ox.com <http://www.ox.com>*
>>>
>>>
>>> *...........................................................................................................................................*
>>>
>>>
>>>
>>> *From:* Chris Kane <ccie14430@gmail.com>
>>> *Sent:* Friday, September 10, 2021 3:16 PM
>>> *To:* Christopher Morrow <morrowc.lists@gmail.com>
>>> *Cc:* Matthew Huff <mhuff@ox.com>; nanog@nanog.org
>>> *Subject:* Re: Never push the Big Red Button (New York City subway
>>> failure)
>>>
>>>
>>>
>>> True EPO story; maintenance crew carrying new drywall into the data
>>> center backed into the EPO that didn't have a cover on it. One of the most
>>> eerie sounds in networking...a completely silent data center.
>>>
>>>
>>>
>>> -chris
>>>
>>>
>>>
>>> On Fri, Sep 10, 2021 at 2:48 PM Christopher Morrow <
>>> morrowc.lists@gmail.com> wrote:
>>>
>>>
>>>
>>>
>>>
>>> On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff <mhuff@ox.com> wrote:
>>>
>>> Reminds me of something that happened about 25 years ago when an
>>> elementary school visited our data center of the insurance company where I
>>> worked. One of our operators strategically positioned himself between the
>>> kids and the mainframe, leaned back and hit it's EPO button.
>>>
>>>
>>>
>>> Or when your building engineering team cuts themselves a new key for the
>>> 'main breaker' for the facility... and tests it at 2pm on a tuesday.
>>>
>>> Or when that same team cuts a second key (gotta have 2 keys!) and tests
>>> that key on the same 'main breaker' ... at 2pm on the following tuesday.
>>>
>>>
>>>
>>> <quadruple face palm>
>>>
>>>
>>>
>>> not fakenews, a real story from a large building full of gov't employees
>>> and computers and all manner of 'critical infrastructure' for the agency
>>> occupying said building.
>>>
>>>
>>>
>>> Matthew Huff | Director of Technical Operations | OTA Management LLC
>>>
>>> Office: 914-460-4039
>>> mhuff@ox.com | www.ox.com
>>>
>>> ...........................................................................................................................................
>>>
>>> -----Original Message-----
>>> From: NANOG <nanog-bounces+mhuff=ox.com@nanog.org> On Behalf Of Sean
>>> Donelan
>>> Sent: Friday, September 10, 2021 12:38 PM
>>> To: nanog@nanog.org
>>> Subject: Never push the Big Red Button (New York City subway failure)
>>>
>>> NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
>>> OUTAGE ISSUE ON AUGUST 29, 2021
>>> Key Findings
>>> September 8, 2021
>>>
>>>
>>>
>>> https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
>>>
>>> Key Findings
>>> [...]
>>>
>>> 3. Based on the electrical equipment log readings and the manufacturer’s
>>> official assessment, it was determined that the most likely cause of RCC
>>> shutdown was the “Emergency Power Off” button being manually activated.
>>>
>>> Secondary Findings
>>>
>>> 1. The “Emergency Power Off” button did not have a protective cover at
>>> the
>>> time of the shutdown or the following WSP investigation.
>>>
>>> [...]
>>> Mitigation Steps
>>>
>>> 1. Set up the electrical equipment Control and Communication systems
>>> properly to stay active so that personnel can monitor RCC electrical
>>> system operations.
>>>
>>> [...]
>>>
>>>
>>>
>>>
>>> --
>>>
>>> Chris Kane
>>>
>>
>
> --
> The computing scientist’s main challenge is not to get confused by the
> complexities of his own making.
> -- E. W. Dijkstra
>
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
----- Original Message -----
> From: "Adam Thompson" <athompson@merlin.mb.ca>

> Now I'm curious... in all of the DCs and COs I've worked in - to the best of my
> knowledge, I haven't personally tested this! - the EPO button does not switch
> to emergency power. It turns off ALL equipment power in the space - no lights,
> no klaxons, nothing. In simpler setups, the EPO is connected to the UPS so
> anything plugged in to the UPS does dark instantly. In one DC I'm familiar
> with, the EPO switch kills all the UPS output and uses several relays to kill
> commercial power at the same time.
> In some, the room lights were not covered by the EPO switch, in some they were.
> Emergency exit lamps will continue to be lit, as they have internal batteries,
> and are required by building/fire code.
>
> Is it (somewhat) common for an EPO switch to only disconnect commercial power
> and leave local redundant power live? What sort of facilities would have this?

No... I just hadn't had my coffee yet that morning and I crossed the streams.

That should be the response to the *ATS cutover*, not the Molly switch.

If someone hits the Molly button, you don't *need* an alarm. :-}

Cheers,
-- jra
--
Jay R. Ashworth Baylink jra@baylink.com
Designer The Things I Think RFC 2100
Ashworth & Associates http://www.bcp38.info 2000 Land Rover DII
St Petersburg FL USA BCP38: Ask For It By Name! +1 727 647 1274
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
> On Sep 10, 2021, at 1:33 PM, Warren Kumari <warren@kumari.net> wrote:
>
> The utility let them know that they were going to be doing some maintenance work in the area. No impact expected, but out of an abundance of caution, they transfer over to generators. After the utility lets them know that the maintenance work is all finished, they want to switch back. If the generators are "emergency power", and you need to switch back to "utility power", obviously the way to do this must be the big red button, clearly marked as "EMERGENCY POWER OFF", no?!

One of the many stories that came out of 9/11 was a switching center in NY City that had a diesel generator as a power backup - which of course acted as primary when the city power is off. After a few days of operation, it needed to be refueled, so a truck was sent in carrying gasoline. The generator was refueled and restarted, and - oops - diesel != gasoline. So then they needed to bring in a new generator.

Yup, it happens, and it happened.
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
Code requires this here. The intent of the EPO buttons are to immediately disconnect all energized power to the entire facility/building in the event of a critical fault like an electrical fire or electrocution.

Only locally-battery powered low-voltage emergency lighting should still be operating. Often the next step after EPO is to flood the room...
—L.B.

Ms. Lady Benjamin PD Cannon of Glencoe, ASCE
6x7 Networks & 6x7 Telecom, LLC
CEO
lb@6by7.net <mailto:lb@6by7.net>
"The only fully end-to-end encrypted global telecommunications company in the world.”
FCC License KJ6FJJ



> On Sep 15, 2021, at 8:58 AM, Adam Thompson <athompson@merlin.mb.ca> wrote:
>
> Now I'm curious... in all of the DCs and COs I've worked in - to the best of my knowledge, I haven't personally tested this! - the EPO button does not? switch to emergency power. It turns off ALL equipment power in the space - no lights, no klaxons, nothing. In simpler setups, the EPO is connected to the UPS so anything plugged in to the UPS does dark instantly. In one DC I'm familiar with, the EPO switch kills all the UPS output and? uses several relays to kill commercial power at the same time.
> In some, the room lights were not covered by the EPO switch, in some they were. Emergency exit lamps will continue to be lit, as they have internal batteries, and are required by building/fire code.
>
> Is it (somewhat) common for an EPO switch to only disconnect commercial power and leave local redundant power live? What sort of facilities would have this?
>
> -Adam
>
> Adam Thompson
> Consultant, Infrastructure Services
>
> 100 - 135 Innovation Drive
> Winnipeg, MB, R3T 6A8
> (204) 977-6824 or 1-800-430-6404 (MB only)
> athompson@merlin.mb.ca <mailto:athompson@merlin.mb.ca>
> www.merlin.mb.ca <http://www.merlin.mb.ca/>
> From: NANOG <nanog-bounces+athompson=merlin.mb.ca@nanog.org> on behalf of Jay R. Ashworth <jra@baylink.com>
> Sent: September 11, 2021 22:23
> To: nanog <nanog@nanog.org>
> Subject: Re: Never push the Big Red Button (New York City subway failure)
>
> ----- Original Message -----
> > From: "Sean Donelan" <sean@donelan.com>
>
> > NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
> > OUTAGE ISSUE ON AUGUST 29, 2021
> > Key Findings
> > September 8, 2021
> >
> > https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf <https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf>
> >
> > Key Findings
> > [...]
> >
> > 3. Based on the electrical equipment log readings and the manufacturer’s
> > official assessment, it was determined that the most likely cause of RCC
> > shutdown was the “Emergency Power Off” button being manually activated.
>
> I don't even *do* datacenter for a living, and I know that when you hit the
> Molly button,
>
> 1) A Klaxon goes off in the Data Center -- one that sounds *different* from
> the Halon Klaxon, in both cadence and tone (just for a couple bursts), and
>
> 2) Yellow rotating beacons turn on, and stay on while you're on Emergency Power.
>
> Yes, real honest-to-ghod *rotating mechanical beacons*, none of this flashing LED
> crap.
>
> Clearly, it's important that the use of Emergency Power be annoyingly noticeable.
>
> Cheers,
> -- jra
> --
> Jay R. Ashworth Baylink jra@baylink.com
> Designer The Things I Think RFC 2100
> Ashworth & Associates http://www.bcp38.info <http://www.bcp38.info/> 2000 Land Rover DII
> St Petersburg FL USA BCP38: Ask For It By Name! +1 727 647 1274
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Wed, Sep 15, 2021 at 3:20 PM Fred Baker <fredbaker.ietf@gmail.com> wrote:

>
>
> > On Sep 10, 2021, at 1:33 PM, Warren Kumari <warren@kumari.net> wrote:
> >
> > The utility let them know that they were going to be doing some
> maintenance work in the area. No impact expected, but out of an abundance
> of caution, they transfer over to generators. After the utility lets them
> know that the maintenance work is all finished, they want to switch back.
> If the generators are "emergency power", and you need to switch back to
> "utility power", obviously the way to do this must be the big red button,
> clearly marked as "EMERGENCY POWER OFF", no?!
>
> One of the many stories that came out of 9/11 was a switching center in NY
> City that had a diesel generator as a power backup - which of course acted
> as primary when the city power is off. After a few days of operation, it
> needed to be refueled, so a truck was sent in carrying gasoline. The
> generator was refueled and restarted, and - oops - diesel != gasoline. So
> then they needed to bring in a new generator.
>

Oooof. I've seen someone at a gas station do something similar -- I cannot
remember if it was putting diesel in their gasoline car, or gas in their
diesel pickup, but I *do* remember the sudden yelp and look of dismay when
they suddenly realized what they were doing. It must be really easy to get
wrong in a car (operating on autopilot), but that's a much less bad failure
than a generator...

Anyway, refueling generators reminds me of:
https://www.mail-archive.com/nanog@nanog.org/msg111947.html

W


>
> Yup, it happens, and it happened.



--
The computing scientist’s main challenge is not to get confused by the
complexities of his own making.
-- E. W. Dijkstra
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On Wed, Sep 15, 2021 at 12:32 PM Warren Kumari <warren@kumari.net> wrote:
> Oooof. I've seen someone at a gas station do something similar --
> I cannot remember if it was putting diesel in their gasoline car,
> or gas in their diesel pickup, but I *do* remember the sudden
> yelp and look of dismay when they suddenly realized what they
> were doing. It must be really easy to get wrong in a car (operating
> on autopilot), but that's a much less bad failure than a generator...

The diesel nozzle has a larger diameter than the gasoline one. It
doesn't fit in the filler neck of a normal gasoline-powered car.

Regards,
Bill Herrin



--
William Herrin
bill@herrin.us
https://bill.herrin.us/
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
> On Sep 15, 2021, at 2:20 PM, Fred Baker <fredbaker.ietf@gmail.com> wrote:
>
> One of the many stories that came out of 9/11 was a switching center in NY City that had a diesel generator as a power backup - which of course acted as primary when the city power is off. After a few days of operation, it needed to be refueled, so a truck was sent in carrying gasoline. The generator was refueled and restarted, and - oops - diesel != gasoline. So then they needed to bring in a new generator.
>
> Yup, it happens, and it happened.

I distinctly remember something like this - Someone built a datacenter with large fuel storage tanks in the basement and the actual generators up on the roof, or some higher floor. It was tested several times, everything seemed to be working as expected, and life went on. Then one day the power went out, the generators came on, but after about 10 minutes the generators started to crap out. It was then discovered that they had forgotten to include the transfer pumps for getting the fuel up from the basement to the generators in the list of things powered by said generators…
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
On September 15, 2021 at 13:31 warren@kumari.net (Warren Kumari) wrote:
> Well, there is the EPO button, which generally does that, and the (variously
> labeled) HALON/FM-200/GAS FIRE SUPPRESSION/GAS DISCHARGE button, which does the
> flashy lights and klangly bell and similar. This is fairly much always required
> by code, to give people time to evacuate before the gas dumps and they
> suffocate.

People don't suffocate from Halon dumps, I've been thru a couple (not
me personally but staff, I was in my office but arrived quickly.)

What is somewhat dangerous about Halon (or likely more modern) fire
suppression dumps is they create like 90mph winds so you're in some
danger from something like a pencil nearby. Hence, cover your face
with your arms or a coat or similar if one is imminent.

It makes a truly impressive mess of a machine room, piles of paper for
example basically tossed out to the walls etc.

But better than a fire. Same for people, better than being roasted
alive or having to breathe burning plastics etc.

People who complain about these systems always seem to pose it like if
it wasn't for the fire suppression system we'd all be much better off,
like if not for these damn lifeboats we could just stay on the ship.

Granted in those two cases nothing very dangerous was going on. Once
it was caused by a nearby security person's walkie-talkie -- yeah, we
proved that by reproducing it tho w/ the hold button pressed so it
wasn't a theory.

--
-Barry Shein

Software Tool & Die | bzs@TheWorld.com | http://www.TheWorld.com
Purveyors to the Trade | Voice: +1 617-STD-WRLD | 800-THE-WRLD
The World: Since 1989 | A Public Information Utility | *oo*
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
Miy story in the late 1970s I was working in a large computer facility
with both mainframes and mil-spec 400hz computers.
Management decided that the EPO should be tested.  So we powered down
the disk and tapes.  The electrician pressed
the EPO button and NOTHING.  Everything kept running.

Turns out a wire had come loose and the fuse in the EPO circuit had blown.

Roy
Re: Never push the Big Red Button (New York City subway failure) [ In reply to ]
----- On Sep 15, 2021, at 9:08 PM, bzs bzs@theworld.com wrote:

Hi,

> People don't suffocate from Halon dumps, I've been thru a couple (not
> me personally but staff, I was in my office but arrived quickly.)
>
> What is somewhat dangerous about Halon (or likely more modern) fire
> suppression dumps is they create like 90mph winds so you're in some
> danger from something like a pencil nearby. Hence, cover your face
> with your arms or a coat or similar if one is imminent.

I can speak from experience. Back in the early 2000s I was working for
a small regional ISP that provided colocation services in the same
building as the office was. We had an Inergen system and I had the
honor of being in the room when it suddenly went off without warning.

The noise and air movement was similar to the one time I rode a
motorcycle on the autobahn and hit 200mph. Not fun. Afterwards I felt
slightly lightheaded, but was otherwise ok. Not that my boss cared,
he lighted a piece of paper outside of the room, walked in, and noted
that, after the flames died out, "hey, it works".

Thanks,

Sabri