Re: Mae-WEST [ In reply to ]
I don't know, but I'll inquire.

James

At 05:06 PM 7/11/97 -0400, you wrote:
>> MFS is in the proccess of installing new cooling units on the roof. They
>> take up aprox. 1000sqft. So they are at least working on it.
>>
>> You should have seen the air lift :)
>>
>>
>
>Any idea what the capacity of the additional equipment?
>
>Thanks.
>
>-Deepak.
>
>

James McKenzie
mcs@innetix.com
Innetix, Inc.
(408) 993-9477
http://www.innetix.com
Re: Mae-WEST [ In reply to ]
At 8:20 PM -0400 7/11/97, Alex Rubenstein wrote:
>According to nitrous.digex.net for its mae-west router:
>
> card inlet hotpoint exhaust
>RSP(4) 26C/78F 38C/100F 44C/111F
^^^^^^^
This is the problem. MFS doesn't have proper cooling if the air if the
ambient air is this hot. It should be no higher than between 15C and 18C in
an equipment room like that.

********************************************************
Michael Dillon voice: +1-415-482-2840
Senior Systems Architect fax: +1-415-482-2844
PRIORI NETWORKS, INC. http://www.priori.net

"The People You Know. The People You Trust."
********************************************************
Re: Mae-WEST [ In reply to ]
On Fri, Jul 11, 1997 at 08:39:08PM -0700, Michael Dillon wrote:
> At 8:20 PM -0400 7/11/97, Alex Rubenstein wrote:
> >According to nitrous.digex.net for its mae-west router:
> >
> > card inlet hotpoint exhaust
> >RSP(4) 26C/78F 38C/100F 44C/111F
> ^^^^^^^
> This is the problem. MFS doesn't have proper cooling if the air if the
> ambient air is this hot. It should be no higher than between 15C and 18C in
> an equipment room like that.
>
> ********************************************************
> Michael Dillon voice: +1-415-482-2840
> Senior Systems Architect fax: +1-415-482-2844
> PRIORI NETWORKS, INC. http://www.priori.net
>
> "The People You Know. The People You Trust."
> ********************************************************

Michael, c'mon...

15-18C? 19C is 66F -- that's very acceptable. 15C would be 59F!

In fact, 68F (at 40% RH) is pretty "standard" for most equipment rooms.
We're config'd for a setpoint of 67F +/- 1F and 40% RH +/- 3%.

One of our more heavily loaded 7513s shows at present:

card inlet hotpoint exhaust
RSP(6) 19C/66F 29C/84F 25C/77F

That's right where it should be.

BTW, exhaust temperature above hotpoint (which your stats show) is *not* a
good thing. I'd find out what's going on there -- you may have some kind
of obstruction with the airflow.

--
--
Karl Denninger (karl@MCS.Net)| MCSNet - The Finest Internet Connectivity
http://www.mcs.net/~karl | T1's from $600 monthly to FULL DS-3 Service
| 99 Analog numbers, 77 ISDN, http://www.mcs.net/
Voice: [+1 312 803-MCS1 x219]| NOW Serving 56kbps DIGITAL on our analog lines!
Fax: [+1 312 803-4929] | 2 FULL DS-3 Internet links; 400Mbps B/W Internal
Re: Mae-West [ In reply to ]
Just got through with the MFS folks looks like we are on master ticket
number 96565. And the person that I was talking with said that,
"There was a rectifer failure in one of the battery rooms at 8:17CT"

If anyone has any other updates, please advise.

T..S

On Wed, 16 Jul 1997, Dave Rand wrote:

> [.In the message entitled "Mae-West" on Jul 16, 9:26, "Todd R. Stroup" writes:]
> >
> > So is there construction at Mae-West again or should I consider flying to
> > SanJose?
> >
> > Todd R. Stroup
> > Fiber Network Solutions, Inc.
>
> We're down a number of places too..
>
> --
> Dave Rand
> dlr@bungi.com
> http://www.bungi.com
>
Re: Mae-West [ In reply to ]
Not that I would suggest using them over the whole nanog list, but, um,
do the mae-west-techs@uu.net (or was it mae-west@ and cix-techs@... i forget)
list and its siblings still work?

Sean.
Re: Mae-West [ In reply to ]